Q. Sir,
in our rectifier we are using aluminium busbar and copper bus bar.
the size of aluminium bus bar is 8inch x 1/2 inch three together .
the copper is 4inch x 1/4 inch . The current carrying capacity 4000 Amps. dc and voltage is 24 vdc . The problem that we are facing is joints are getting heated up . There are six bolts for joining . please suggest as to what should be done in order to reduce heating effect
Kamaljit Singh Gill
production - Jamshedpur, Jharkhand, India
A. Heat-up at joint area is because the bolts and nuts, I guess you use ss.
John Hu
A. Probably, oxide on the aluminum surface resulted in electrical resistance causing heating and further oxidation... I will presume that the 3 aluminum bars are interleaved between 4 copper bars (minimum for 4000 Amps), perhaps in a right angle connection, and that this joint is compressed together with a single set of 6 bolts.
Ideally, the aluminum contact areas are plated with silver.
A less expensive alternative is to clean and protect the contacts as follows: Remove the oxide from contact areas, either chemically or by very fine grit sanding, apply electrical joint compound (EJC) such as Alcoa No. 2, then use a stainless steel brush or emery cloth to lightly abrade the aluminum surface working through the EJC layer(to expose bare metal while preventing oxidation). Also clean the copper contacts. Then, the joint should be assembled with a clamping pressure of 1000 psi. This reduces the contact resistance to 0.5 micro-ohm/sq. inch according to Figure 53 in the Alcoa Aluminum Bus Conductor Handbook. Presuming a 2 x 3 bolt pattern in an 8x4 inch contact area, use 1/2-inch bolts tensioned to 6000 lbs along with heavy flat washers and stainless steel Belleville washers (which maintain the load over time). If available, use high-strength aluminum fasteners lubricated with EJC; if not, use ASTM A325 steel or equivalent.
See also Letters #7897, 29456, 39557, 40211 dealing with aluminum bus bars.
Ken Vlach [deceased]
- Goleta, California
A. Dear Kamaljit Singh Gill ,
Check the following points,
1) 8 x 1/2 aluminium will carry around 3000 amps current. You are using 3 bus bars that means capacity will be 9000 amps
2) 4 x 1/4 copper will carry 1000 amps current,so increase the no of bus bars up to 4, because you have to carry 4000 amps current so you need 4 bus bars of copper.
3) At joints there will be resistance because of air gap, ensure that all bolts are tight.
You implement this you are problem will be gayab......
vishwas nangare
Vishwas Nangare
motorcycle accessories mfgr.
- Aurangabad, Maharashtra, India
Q. Sir,
We are using mild steel nuts and bolts to hold aluminium and copper bus bars. As Mr. John Hu.
I guess it would be the cause. I would request Mr.John Hu to suggest which coated bolts I should use to eliminate the problem of AL-CU joint heating .The joint is carrying current of 3500 Amp. DC and voltage is 24 VDC.
regards
K.S.Gill
kamaljit singh gill [returning]
- jamshedpur,jharkhand, India
A. Do as what Mr. Ken Vlach say,but I still recommend you to plate the bolts and nuts with tin too, not use ss, let alone mild steel, doing so you will greatly prevent the contacting area from oxidation or corrosion.
John Hu
A. RESISTIVITY OF ALUMINIUM AND COPPER IS DIFFERENT. SO KEEPING THAT IN MIND WHENEVER THERE IS AN CHANGE IN RESISTANCE OCCURS IN TNE PATH OF A ELECTROMAGNETIC WAVE REFLECTION AND REFRACTION OF WAVE OCCURS DUE TO WHICH CHANGE IN VOLTAGE AND CURRENT LEVEL OF CONDUCTOR OCURES WHICH CAN UNBALANCE THE SYSTEM .. (LIKE HEATING )
SO WHY WE GO FOR THIS TYPE OF JOINTING?
PLEASE GIVE CLEAR BASIC IDEA ABOUT IT.
DHANANJAY PANDEY
Electrical Engineer - RAIPUR, CHHATTISGARH, India
May 24, 2008