Q. This question pertains to drop in pH of blowdown water of a low pressure steam boiler.
In one of the waste heat recovery boilers, (operates at 180 °C), pH of the blow down water drops to 5 and even 4. The feed water is maintained around a pH of 9 and the water is treated with trisodium phosphate [on eBay or Amazon (adv.)] along with other inhibitors. The pH of the feed water is adjusted with sodium hydroxide [affil links]. (Note the process side is maintained at a very low pressure)
Analysis reveals that the total organic content of the feed water lies around 8-10 ppm.
What is the role of TOC? can this cause such a drop in pH?
If not what is the problem?
Raja
VS Raja
- Mumbai, MA, India
A. Without a treatment to keep the pH elevated in the condensate, you will always see a reduction in pH in the steam lines and consequently the condensate. This is due to a buildup of Carboxylic Acid as a reaction of carbon dioxide which is dissolved in the water. People will typically use amines as a steam line treatment because it volatilizes and keeps your pH elevated. You want your condensate to have a pH of 8-8.5. pH lower than that can lead to severe corrosion that you will not be aware of until your steam lines have been ruined. Get that pH up in the condensate as soon as possible. Depending on the pH and time and temperature, it can lead to catastrophic failure of your system.
The organic compounds have no effect on the pH of your boiler. They are naturally occurring in surface waters which is probably the source of your incoming water.
I would contact a water treatment chemical supplier in your area to get professional assistance which should be part of your chemical purchasing process.
Daryl Spindler
Daryl Spindler, CEF
decorative nickel-chrome plating - Greenbrier, Tennessee
A. How many hours can you run boiler with the pH is 5 and 4?
Mathias Po
- philippines
January 27, 2013
Q. I would like to add on his question in relation to our plant. we have a high pressure boiler but we minimize our blowdown in relation to silica and pressure. in two months time without blowdown, we have observed decreasing pH in the feed and boiler water even with 2-3 ppm phosphate. our treatment if ammonia [on eBay or Amazon (adv.)] and hydrazine at the feedwater and TSP for the boiler. is this due to TOC or acid conditions at the boiler due to concentrating minerals.
Thank you very much for your immediate response.
Rizza L. Ocsan
- Dagupan, Philippines
Ed. note: We are very pleased to print your followup question, Rizza. But for urgent needs please contact your supplier, or retain an independent consultant. This is a public forum where the readers who are most capable of answering your question well may not even see it for weeks -- we have no power to summon them. Thanks!
Q. Sir,
We have operating 108 bar pressure boiler. Some times drum water pH dropped at level 7.5,but at the same time feed water pH, steam pH, and condensate pH were normal (above 8.4).
What is the reason for this problem.
K.G.Sivakumaar
asst manager - erode, Tamil Nadu, India
November 30, 2009
Q. I am working in a boiler (17.5 Kg/Cm square) where boiler feed water pH is 8.5 but boiler blowdown pH is dropped to 7.5-8.0. My question is if boiler feed water pH is ok then what cause can be responsible to drop the pH of blow down.
Ajit Mondal
chemical engineer - Haldia, India
May 31, 2011
A. Dear friends,
I am also working in a 90 ksc boiler system. My experience and few consultants say that drum water (blow down water) lowering due to more iron content in feed water (during commissioning) where iron will eat away the phosphate (TSP hydrolysis will be affected and no caustic to raise the pH).
More TOC (> 1 ppm) in feed water will contribute to lowering pH due to formation weak acids (organic) due to decomposition of TOC at 350 deg. C. During this time if add caustic (2% solution at minimum level based on blow down) pH will increase; this is due to the formation of NaOH from TSP is consumed by weak acids and the external addition NaOH used for increase the pH.
Kumar Pavadai
- Salem, Tamil Nadu, India
October 20, 2011
Q. Some of the power plants like super critical oxygen is getting injected in feed water to ACC corrosion and 150 ppb residual is being maintained in feed water. Is it advisable?
Because we are (90 ksc) force remove DO through mechanical de-aerating system as well as chemical treatment to achieve 7 ppb.
Kumar Pavadai [returning]
Chemical engr - Salem, Tamil Nadu, India
October 20, 2011
Q. I am working in a power industry of 500 MW unit and the drum pressure is around 190 Kg/cm2. I am facing the problem i.e., the drum pH is gradually in decreasing tendency i.e., around 4.4 and the phosphate reserve is < 1.0 and the pH and conductivity of the feed, condensate and steam values are in normal range i.e., pH - 8.9 and conductivity is 4.5 to 5.0. We are dosing tri-sodium phosphate to the drum, hydrazine and ammonia at feed section. Our limits for feed & steam are in the range 8.8 to 9.2 and for drum 9.1 to 9.7. We are in hurry. Please feel free to attend this problem at the earliest.
R.P.Rao
- Visakhapatnam, AP, India
March 17, 2012
Q. Our (AFBC) boiler is 89 tph and pr is 88 kg/cm; we maintain TSP in boiler 12 ppm but our design limit is 20 ppm and maintain pH 9.5. So tell me about effect of low TSP dosing and maintaining low parameter.
Naresh Menaria
- Nimbahera, Rajasthan, India
June 4, 2012
pH of Boiler Blowdown Water
I am wondering how much will blow down pH be if we use raw water that has 6.9 pH to create 75% quality steam?
Abdu Ahmed
- Fort Mcmurray Canada
November 10, 2015
Q. Sir,
We have operating 45 KG/CM2 pressure boiler. Sometimes drum water pH dropped at level 6.5, but at the same time feed water pH, steam pH, and condensate pH were normal (above 8.4).
What is the reason for this problem?
GIRISH DWIVEDI, General Manager PP
- BALRAMPUR, UTTAR PRADESH, India
January 4, 2016
A.
• Check dosing chemicals quality
• Check 2P "M value" if it is too low, then that may also create low pH condition.
• Check hot well cationic conductivity; feed water hardness
• Check MB outlet to ensure that there is no accidental contamination of regeneration chemical
Ansuman Sen Sharma
- Vadodara, Gujarat, India
February 17, 2016
pH rises between feedwater tank and boiler
Please I want to know what can really be responsible for increase in pH from feed water tank to boiler water because, where I work, the boiler water pH is always higher than feed water.
THOMAS OLAWUNMI
- Apapa, lagos, Nigeria
March 31, 2016
A. Hi Thomas. Your question will probably be more answerable and draw better responses if you make it less vague, with data such as the pH of the feedwater and of the boiler.
pic of Ted Mooney
March 2016
Anyone know the probable cause of different pH of the feed water and the boiler water? I'm getting a pH of more than 9 in the feed water, while in the boiler water I'm getting almost 11.80. Thanks.
EMMANUEL BAUTISTA
- Jubail, Saudi Arabia
January 4, 2017
Q. We are Getting the drum water pH Below 9.0 always even the feedwater pH level is above 9.1.and Hydrazine residual levels Maintaining More Than limit for avoiding DO.
Venkatesh kumar
- Kakinada, Andhrapradesh, India
January 21, 2017
A. What I feel is that boiler pH can get down with entrance of exhaust in the boiler water as it totally contains CO & CO2; they can create carbonic acid which can contribute these amount of pH drop. So, better you check your exhaust gas lines whether there is any leakage which is allowing exhaust gas to enter into water.
MOHAMMAD HASIBUL HASAN
Buckman, Water treatment chemical & solution provider - Dhaka, Bangladesh
October 6, 2017
Q. We have HRSG [Heat Recovery Steam Generator] with three drums LP [low pressure], IP [intermediate] and HP [high]. Pressure of HP drum is 120. We have facing problem of low pH (5-8) and Low PO4 in HP drum in spite of continuous dosing of Tri Sodium Phosphate. Conductivity of boiler water is also high, i.e., about 200 µs/cm. While Feed, Hot well condensate pH and steam pH is ok. We're dosing ammonia and Hydrazine in feed water system.
Besides this, Sio2 in both IP and HP Boiler water is higher than Limit, i.e., above 100-200 µg/l. but SiO2 in feed and in our demi storage is within limit, i.e., less than 10 µg/l
Please solve our problem; what are the causes:
1. pH and PO4 is not maintaining in HP boiler.
2. High conductivity of Boiler water.
3. High SiO2 in Boiler water.
Fazal Khan
- Sukkur Pakistan
December 29, 2017
A. You are facing a problem called "phosphate hideout" and to solve this problem follow the following steps:
1. Increase blowdown up to 50%
2. Check Iron in the drum and the superheat
If you found Iron in the drum more than the limit, you must contact with engineers to schedule outage of station as soon as possible.
Most phosphate hideout problems have no solutions; the only solution is the station outage.
Ahmed Mahfouz
- Egypt, Cairo
January 22, 2018
Q. I AM A CHIEF CHEMIST IN A SUGAR FACTORY MY Q IS, IS THERE ANY POSSIBILITIES FOR DROP IN pH IN EXHAUST CONDENSATE WITHOUT CONTAMINATION? IF SO WHAT ARE THE REASONS?
POLAVARAPU GOPALA KRISHNAMA NAIDU
SUGAR INDUSTRY - BOBBILI, ANDHRA PRADESH, India
February 22, 2018
pH increase in blowdown of steam generator?
Q. We have steam generator feed with water of pH 9.5 and this pH suppose to be decrease in the blowdown because of high heat and forming of carboxylic acid.
But in our case the pH in the blow down is increase up to 11.8 which is creating lot of issues for us.
Really I don't understand why pH increase in the blowdown? If anybody has an idea why it's happening it will be of a great help?
Mubarak Said
- Oman
July 31, 2018
Q. In medium pressure boiler, feed water quality DM water pH is maintained by chemical but blow down water pH tested less than 7 -- what are reasons?
Neeraj Kumar
- New Delhi, Delhi (India)
March 16, 2019
A. Folks, "ph drop in boiler blowdown" question has been the main theme of this thread. Can you respond in terms of the proposed explanations & solutions already offered please? Ignoring the responses and simply starting over is usually the kiss of death to a topic.
pic of Ted Mooney
March 2019
Q. Boiler water programs are based on three main areas and the treatments and due diligence to each can help avoid many issues.
(1) External makeup water is one of the three main parameters and can have conditions that could include the quality of the condensate return, changing raw feed source water conditions (high hardness water or RO, DI soft water), softener brine regeneration rinse contamination treatments and along with de-aerators are some factors that could all play a role in the external feed makeup water quality.
The (2) second main area is in the actual internal boiler water conditions and these treatments can be affected by carryover of wet steam from too rapid a demand for steam for a small boiler, improper or low water treatment to address changes in bicarbonate and carbonate alkalinity and contamination from a waste heat gas getting into the water from a fault in the heater tubing and or a simple leak.
The (3) third main area of a boiler waterside program is in the condensate treatment and the quality and amount of condensate used and how any condensation is neutralized as the steam condenses back into water as any unused steam is condensed and is returning to the makeup tank. Under low fire conditions, a leaky heat exchanger could be drawing some contaminates into the condensate and this could lower the feed makeup water pH unknowingly, a leaky seal on a suction side of a pump could be introducing air and causing some lowering of pH, the type and amount of neutralizing amine used to protect the condensate could be off and not carrying the ideal corrosion protection the full length of the condensate system.
I might recommend that your team consider trying to start increasing the alkaline feed builder product in your boiler water treatment into the makeup tank to drive up the pH and then watch for issues where demand for steam might cause excess wet steam carryout lowering your water treatment on the internal side. If your team put a conductivity meter on the condensate line return you could see if the quality of your steam matches what you think and at the same time get a good idea where and when you might be carrying some tramp contaminates back into your condensate return from a faulty heat exchanger, bad steam trap and don't be surprised if your team might discover that you have some other water from a possible bad connection or crossover lines in your process.
If you could fill in some additional thoughts on what your team does in each of the three main treatment areas and if you experience low water alarms / wet steam issues or contamination in the condensate that would help pinpoint some possible reasons why your boiler internal water conditions pH is dropping. What is the steam actually used for and how much condensate return is part of the actual makeup water ( for example ... do you get 50 % of your makeup water from the condensate or 10 % ... or for example if you are steam heating urea or heating a phosphate bath in a coil could you be dragging some tramp urea or acidic bath liquid into the condensate through a fault in the coil ... I guess what are you doing to what? )
Brian Lamphron
- Sioux Falls, South Dakota